  • #5600

    In this wiring diagram, I see a single 14G wire going to two poles of the switch. What exactly does this mean? Will it be fine if I connect each wire to a single pole and leave two open?

    Attachments:
    You must be logged in to view attached files.
    #5602
     SuperDroid
    Keymaster

    Hi,
    In the schematic that is a 4 pole switch and each pole is rated at 25A, we have a 30A fuse in each wire, this means that the switch could burn before the fuse pop, we connected 2 poles to divide the current. But you can connect 1 wire per pole no problem or you can bridge all 4 poles together.